I'm confused, but I assume you're referring to skin effect, which is a function of
frequency. The diameter of the wires in the cords in question is small compared to the skin depth in copper at 50/60Hz, so the resistance wouldn't be significantly higher than at DC. PSUs without APFC will produce harmonic distortion but this still shouldn't make the skin effect noticeable.
For what it's worth, the official current ratings for flexible cables could be said to be somewhat marginal, given the rather low ambient temperatures assumed (25–30°C). (The maximum conductor temperature allowed for
flexing PVC-insulated cables is 60°C even though the rated temperature may be higher, because PVC gets soft when hot.)
Official ratings (correct me if I'm wrong):
0.5mm²: 3A
0.75mm²: 10A (
up to 2m)*/7.5A (Australian standard)
1.0mm²: 10A
1.5mm²: 16A
2.5mm²: 25A
These are for single-phase, de-rate by 18% for three-phase circuits.
*That's a somewhat problematic specification as the IEC-type cords can be chained, enabling the 2m limit to be exceeded. And the cord that came with my current monitor has 0.75mm² conductors despite being longer than 2m. So the enforcement is rather lacking.I would prefer to stay within
these limits (which I admit to making up, but should be reasonably accurate assuming an ambient temperature of 40°C):
0.75mm²: 6.7A 1-phase/5.4A 3-phase
1.0mm²: 8A 1-phase/6.7A 3-phase
1.5mm²: 10A 1-phase/8A 3-phase
2.5mm²: 16A 1-phase/13A 3-phase
I dunno about 0.5mm². It seems to be only barely acceptable (assuming a C16 circuit breaker upstream) for small loads. I've never seen a detachable cord legitimately using it, anyway (even though it would theoretically be adequate for the C7/C8 couple).
This doesn't mean I would actually enforce my standard any time soon, as until we end the tradition of bundling the cords with each new appliance, it would mean more wasted copper.
I don't know if the new-fangled mPPE (modified polyphenylene ether) insulation (not yet used for mains cords, but available for hook-up wire and communication and control cables from
one manufacturer) softens when hot like PVC does. But I guess it would be a bad idea to let the cords get too hot to touch even with insulation that
can take the heat.
So I would suggest to award bonus points to PSUs that make the cord optional (or simply don't include one).
That latter version may be a tad controversial though…